Mariëlle,
I would recommend trying with Type108 instead of Type8. You can use the 1st stage cooling setpoint as your night ventilation. You may also want to multiply the Type108 output by the result of another equation to make sure that night ventilation isn't activated during the daytime.
Best,
david
Mariëlle Nuchelmans wrote:
Hi all,
I want to model a nightventilation system with following setpoints:
Switch on when roomtemperature is 23 degrees, switch off when roomtemperature is below 19 (hysteresis)
I use type8b. But it only gives a coolsignal when I set the deadband on 0 degrees, but I should set it on 4 degrees. But then I never get a coolsignal. What am I doing wrong?
Met vriendelijke groet,
Mariëlle Nuchelmans
________________________________
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu<mailto:TRNSYS-users at cae.wisc.edu>
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com<mailto:bradley at tess-inc.com>
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100416/05068c40/attachment-0001.htm>
More information about the TRNSYS-users
mailing list