[TRNSYS-users] Nigh time spray radiant cooling
David Bradley
bradley at tess-inc.com
Tue Apr 6 11:59:36 PDT 2010
Patrick,
I would think that the correct way of going about it (in TRNSYS) would
be to write a model of the wetted outermost layer of the roof to take
into account the evaporation, convection, and radiation that occurs at
all times (night or day) and then couple it to a BOUNDARY wall (that
models the remaining roof layers) . We've used the concept in the past
to model PCM wall materials and to model ground coupling.
Best,
David
Patrick Wilkinson wrote:
>
> *Has anyone modeled a nighttime radiation cooling system, where the
> water is sprayed directly on the rooftop of the building, not through
> tubing/flat plate collectors? If so, any ideas on how to model this in
> TRNSYS/Excel?*
>
> * *
>
> *Any information on the theoretical background would also help. I can
> only seem to find information regarding closed systems.*
>
> * *
>
> *thanks*
>
> Patrick Wilkinson, P.E., LEED^® AP
> Advanced Technology Group
>
>
>
>
> 14130 Riverside Drive Suite 201
> Sherman Oaks, CA 91423
> p: (818) 377-8220 ext. 240
> f: (818) 377-8230
> www.ibece.com
>
>
>
>
>
>
>
> This e-mail message, including any attachments, is for the sole use of
> the intended recipient(s) and may contain confidential and privileged
> information. Any unauthorized review, use, disclosure, or distribution
> is prohibited. If you are not the intended recipient, please contact
> the sender by reply e-mail and destroy all copies of the original message
>
>
>
> .
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100406/4a5a114a/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2407 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100406/4a5a114a/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20100406/4a5a114a/attachment-0003.jpeg>
More information about the TRNSYS-users
mailing list