A running average type is type84. I have found a bug in a past version which
david repaired so make sure yours is the newest construction.
Good luck,
John Bisgrove
Earth Sensitive Solutions
7523 County House Road
Auburn, NY 13021
(315)253-3779
_____
From: David Bradley [mailto:bradley at tess-inc.com]
Sent: Friday, October 02, 2009 10:16 AM
To: P. Demircian
Cc: trnsys-users at cae.wisc.edu
Subject: Re: [TRNSYS-users] 24h mean value of operative room temperature
Type55 will generate the mean value over a 24 hour period (for example
midnight to midnight) and then reset at the end of that period. If your
controls are based on what the previous day's mean operative temperature
was, you can do it with Type55. If, on the other hand, you want to control
based on a running average over the past 24 hours, you'd have to use a
different Type. A running average component will be included in TRNSYS 17.
Regards,
David
P. Demircian wrote:
hello .. ,
I want to use the 24h mean value of my operative room temperature too
control my cooling system (Active Layer), The problem is that i have no clue
how too do this, I am using Trnsys 16 Studio and try it with TYPE 55..has
any one a clue how to do it.
Best Regards Petros
Mit freundlichen Grüßen
P.Demircian
fischer energie + tga consult
Ingenieurgesellschaft mbH
Dieselstraße 18
61191 Rosbach
Telefon: 06003 93504-0
Telefax: 06003 93504-22
E-Mail: p.demircian at fIscher-tgaconsult.de
_____
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091002/7170435c/attachment-0005.htm>