Type55 will generate the mean value over a 24 hour period (for example 
midnight to midnight) and then reset at the end of that period. If your 
controls are based on what the previous day's mean operative temperature 
was, you can do it with Type55. If, on the other hand, you want to 
control based on a running average over the past 24 hours, you'd have to 
use a different Type. A running average component will be included in 
TRNSYS 17.
Regards,
 David

P. Demircian wrote:
>
> hello .. ,
>
> I want to use the 24h mean value of my operative room temperature too 
> control my cooling system (Active Layer), The problem is that i have 
> no clue how too do this, I am using Trnsys 16 Studio and try it with 
> TYPE 55..has any one a clue how to do it. 
>
>  
>
> Best Regards Petros
>
>  
>
> Mit freundlichen Grüßen
>
>  
>
> P.Demircian
>
>  
>
> *fischer*  .  energie  +  tga *consult* 
>
> Ingenieurgesellschaft mbH
>
> Dieselstraße 18
> 61191 Rosbach
> Telefon: 06003 -- 93504-0
> Telefax: 06003 -- 93504-22
>
>
> E-Mail: _p.demircian at fIscher-tgaconsult.de 
> <mailto:p.demircian at fIscher-tgaconsult.de>___
>
>  
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091002/ddb7361b/attachment-0005.htm>


More information about the TRNSYS-users mailing list