[TRNSYS-users] Type-2b???
Francois Badinier
francois.badinier at icax.co.uk
Wed Nov 25 05:21:20 PST 2009
Hi Francesco
Here is the solution to your problem (see attached modified project):
1. First of all, make sure you connect the output signal of the Type2b to
its "input control function", to ensure a proper hysteresis effect
2. When you want to switch the control signal to 0 when approaching a fix
target/setpoint temperature with lower value (e.g. when controlling a
heating device), you have to use the following procedure:
a. connect your variable temperature to the upper input of
the controller
b. set the same deadband as you did
c. use the opposite of the control signal via a calculator
(either use the function Not(...), or the equation 1-...)
That's the only way I found to use Type2b to do such a control.
Hope this helps.
François Badinier
Development Engineer
ICAX Ltd
1 Hatfield House
Baltic Street West
London EC1Y OST
<mailto:alan.kiff at icax.co.uk> francois.badinier at icax.co.uk
<http://www.icax.co.uk> www.icax.co.uk
-----Original Message-----
From: Besana Francesco [mailto:Francesco.Besana at eurac.edu]
Sent: 25 November 2009 11:06
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] Type-2b???
Dear Trnsys-colleague,
It is unbelievable but I have spend more than one hour on that and still
doesn't work...the point is:
I would like to switch off a signal when the difference between the High
Temp (fix to 22 ) and Low Temp is less than 0 and switch on again when the
difference is higher than 1.5..are you able to do that?
At the moment in my deck (attached) it seems that instead off an hysteresis
loop I have just a value limit 1.5 where is ON and OFF around it!!!
Thanks a lot and suggestions are well accepted
Francesco
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.709 / Virus Database: 270.14.80/2523 - Release Date: 11/25/09
07:31:00
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091125/ad32bd33/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Project6_modified.tpf
Type: application/octet-stream
Size: 67890 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091125/ad32bd33/attachment-0001.obj>
More information about the TRNSYS-users
mailing list