[TRNSYS-users] HEATING / COOLING EQUIPMENT EXTERNAL TO TYPE 56
rgaray at labein.es
rgaray at labein.es
Wed Nov 18 23:45:07 PST 2009
Dear Francisco,
Your statement is true. If you want to control the HVAC systems you state,
it is needed a ventilation or gain heating/cooling system.
For that system to be implemented, you should need the following inputs to
the building type 56:
For the air systems:
- Air change rate (maybe you should calculate this value from the air
flowing inward and the zone volume) (1/h)
- Inlet temperature (ºC)
For the water systems or other non mixing systems:
- Hourly power supplied by the system (if you want, convective and
radiative power can be set separately) (KJ/h)
- Humidity (Kg/h)
As output of the system, this is a very vague question. Depending on your
needs, any of the building variables can be stated as output.
Standard outputs include zone temperatures that may be needed for the HVAC
control system.
I hope this answers your questions.
Suerte!
--------------------------------------------------------------------------
Roberto Garay Martinez
Labein-Tecnalia
Unidad de Construcción y Desarrollo del Territorio
c/Geldo. Parque Tecnológico de Bizkaia
Edificio 700
48160 Derio (Bizkaia)
Tel.: 34 94 607 33 00
Fax: 34 94 607 33 49
www.labein.es
---------------------------------------------------------------------------
Visite nuestro blog:
http://www.energiaenedificacion.com
------------------------------------------------------------------------
Bilbao, 17-19 de Mayo, 2010
Open and Sustainable Building
Edificación Adaptable y Sostenible
www.OpenBuilding-2010.org
--------------------------------------------------------------------------
----- Mensaje de "JUAN FRANCISCO BELMONTE TOLEDO" <JuanF.Belmonte at uclm.es>
en Wed, 18 Nov 2009 13:35:20 +0100 -----
Para:
<trnsys-users at cae.wisc.edu>
Asunto:
[TRNSYS-users] HEATING / COOLING EQUIPMENT EXTERNAL TO TYPE 56
hello everyone.
i´d greatly appreciate your help in this question.
Reading the Manual Vol. 6 (Multizone Building Modeling) and the tutorial
downloadable from the trnsys web, i see clear that to model an external
heating/cooling equipment, heating/cooling type in trnBUILD not should be
used, instead of that it should be used VENTILATION TYPE MANAGER (for air
systems) or GAIN TYPE SYSTEM (for hydronic or refrigerant vapor
compression systems).
IT´S THAT CORRECT?
In this case (hydronic system, in particular boiler + water radiators)
Is necessary supply the type56 with a hot water loop from the boiler?
what INPUTS AND OUTPUTS are required in this case for type 56?, i´m
particularly interested in the OUTPUTS, and its coupling with the hot
water circuit.
thanks a lot.
Juan Francisco Belmonte Toledo
Universidad de Castilla-La Mancha
02071 Albacete. Spain
__________________________________________________________________________________________________________
Imprime solo lo imprescindible, recuerda tu compromiso con el MEDIO AMBIENTE
Behar beharrezkoa baino ez imprimatu, gogoratu zure INGURUGIROArekiko konpromezua
Before printing think about the ENVIRONMENT
__________________________________________________________________________________________________________
Este mensaje se dirige exclusivamente a su destinatario y puede contener informacion privilegiada o confidencial. Si no es vd. el destinatario indicado, queda notificado de que la utilizacion, divulgacion o copia sin autorizacion esta prohibida en virtud de la legislacion vigente. Si ha recibido este mensaje por error, le rogamos que nos lo comunique inmediatamente por esta misma via y proceda a su destruccion.
Mezu honek eta erantsita dituen agiriek (baldin baditu) isilpeko informazioa izan dezakete. Hori dela eta, hutsegite baten ondorioz jasotzen duenak jakin beza bertan dagoen informazioa ezkutukoa dela eta legeak galarazi egiten duela berori baimenik gabe erabiltzea.
This message is intended exclusively for its addressee and may contain information that is CONFIDENTIAL and protected by professional privilege. If you are not the intended recipient you are hereby notified that any dissemination, copy or disclosure of this communication is strictly prohibited by law. If this message has been received in error, please immediately notify us via e-mail and delete it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091119/0926ebc6/attachment-0001.htm>
More information about the TRNSYS-users
mailing list