[TRNSYS-users] Convective heat transfer coefficients of a "large opening" between zones
Erik Olsen
olsen at transsolar.com
Fri Nov 13 07:13:14 PST 2009
Hi Knut Erik
It looks like this is the main question remaining on your greenhouse
simulation.
I would set convection coefficients to zero (or a very small number if
zero isn't accepted), and us a separate method to define the air
exchange between the two zones with a coupling when the screen is open.
The large direct air exchange between the zones renders any convection
coefficient meaningless.
Regards
Erik
knut.erik.enerstvedt at niva.no wrote:
>
> Hello,
>
> I have an ADJACENT window (with shading) between two Type 56 zones to
> model a controlled screen which can be either pulled across or pulled
> away. Does anybody know what the convective heat transfer coefficients
> of the window should be when the screen is pulled away (that is, when
> the window is "gone" and there is just a large opening between the
> zones)?
>
> All help is higly appreciated.
>
> Regards,
> Knut Erik Enerstvedt
> ------------------------------------------------------------------------------------------------------------
> Meld deg på vårt nyhetsbrev på www.niva.no