[TRNSYS-users] Convective heat transfer coefficients of a "large opening" between zones
David Bradley
bradley at tess-inc.com
Thu Nov 12 20:56:27 PST 2009
Knut Erik
I would imagine that your adjacent window is a virtual window, there
only to provide you with the ability to set a shading factor when the
screen is pulled across. If that is the case, I would leave the
convective coefficients for the window alone whether the screen is
pulled or not. I would, however, define a coupling air flow through the
window and set its value differently when the screen is open and when it
is closed. Make sure that you transfer approximately the same amount of
air in both directions (up and down through the virtual window) Knowing
what value to pick for the coupling air flow is difficult. Ideally you
would use one of the airflow models coupled with the Type56 building in
order to assess it (COMIS, CONTAM, or TRNFLOW). However, this isn't an
ideal solution either because those bulk air flow models base their flow
on temperature and pressure differences. In the case of a large
horizontal opening, this means that flow can only go one direction at a
time, which has a tendency to over pressurize either the zone above or
the zone below and cause convergence problems. The most correct solution
is to do some CFD work and learn what the net transfer of air through
the opening is. If that is outside the scope of what you are doing, I
would pick a fairly high air change rate (5ach/h?) and apply that as the
coupling flow when the screen is open.
Best,
David
knut.erik.enerstvedt at niva.no wrote:
>
> Hello,
>
> I have an ADJACENT window (with shading) between two Type 56 zones to
> model a controlled screen which can be either pulled across or pulled
> away. Does anybody know what the convective heat transfer coefficients
> of the window should be when the screen is pulled away (that is, when
> the window is "gone" and there is just a large opening between the
> zones)?
>
> All help is higly appreciated.
>
> Regards,
> Knut Erik Enerstvedt
> ------------------------------------------------------------------------------------------------------------
> Meld deg på vårt nyhetsbrev på www.niva.no
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20091112/5aefc180/attachment-0001.htm>
More information about the TRNSYS-users
mailing list