Claire,
Yes, you can. Use Type11f (the flow diverter where you give it the
control signal) and use the following equation to calculate Y
Y = (Tsetpoint - TColdSource) / (THotWater - TColdSource)
the flow out of port 1 should go to your cold source and the flow out of
port 2 should bypass it and mix back in afterwards.
Kind regards,
David
claire kazgandjian wrote:
> Hi trnsys users,
> usually the type 11b receives cold water in input from the cold
> source, shares this flow and sends a part to the heat source (=>the
> resulting temperature is higher than the input).
> Is it possible to do the contrary : type 11b receives hot water in
> input from the heat source, shares it and sends a part to be cooled to
> a cold source (=>the resulting temperature is lower than the input) ?
>
> Thanks!
>
> Claire
>
> ------------------------------------------------------------------------
> Votre correspondant a choisi Hotmail et profite d'un stockage
> quasiment illimité. Créez un compte Hotmail gratuitement !
> <http://www.windowslive.fr/hotmail/default.asp>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090615/ce436804/attachment-0001.htm>
More information about the TRNSYS-users
mailing list