[TRNSYS-users] Control of on active layer
Cramer Silkworth
silkworth at transsolar.com
Mon Jul 13 06:42:46 PDT 2009
Arnaud,
All you need is an equation:
Tinflow = gt(Tzone,20) * Toutside_amb + not(gt(Tzone,20)) * 35
the GT and LT functions return either 0 or 1, so this contruction gives
you, in effect, an in-else statement.
-Cramer
-----Original Message-----
From: A.Thome-08 at student.lboro.ac.uk
[mailto:A.Thome-08 at student.lboro.ac.uk]
Sent: Sunday, July 12, 2009 8:34 AM
To: Cramer Silkworth
Subject: RE: [TRNSYS-users] Control of on active layer
Good afternoon,
I would like to pre-heat the inflow of the ventilation during the
heating period to see the impact that this would have on the heating
bill.
To do so I would like find a controller to model:
if Tzone>20°C then Tinflow=Toutside_amb
if Tzozne<20°C then Tinflow=35°C
Do you know wich controller should I use?
Thank you very much!
Quoting Cramer Silkworth <silkworth at transsolar.com>:
> Arnaud,
>
> Type 2 is a basic deadband controller with hysteresis ('memory'), set
> a deadband of around 2K, so the heat comes on when the temp drops
> below 20, and goes off when the space hits 22, for example. Use its
> output to control the massflow of the active layer.
>
> There's probably an example of how to use this type in one of the
> example files, it can be a bit confusing at first to figure out all
> the inputs - so check out the examples and documentation.
>
> -Cramer
>
>
> -----Original Message-----
> From: A.Thome-08 at student.lboro.ac.uk
> [mailto:A.Thome-08 at student.lboro.ac.uk]
> Sent: Thursday, July 09, 2009 12:59 PM
> To: trnsys-users at cae.wisc.edu
> Subject: [TRNSYS-users] Control of on active layer
>
>
>
> Good afternoon,
>
> Within type 56, I created an embedded heating floor using an active
> layer.
> But I don't manage to control it.
>
> I would like the heating floor to operate only when the temperature of
> the room is below 20°C.
>
> Which component should I use and how should I connect it.
>
> Thank you very much.
>
> Best regards,
>
> Arnaud T.
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>
More information about the TRNSYS-users
mailing list