Cramer Silkworth silkworth at transsolar.com
Thu Jul 9 11:13:39 PDT 2009


Arnaud,

Type 2 is a basic deadband controller with hysteresis ('memory'), set a 
deadband of around 2K, so the heat comes on when the temp drops below 
20, and goes off when the space hits 22, for example. Use its output to 
control the massflow of the active layer.

There's probably an example of how to use this type in one of the 
example files, it can be a bit confusing at first to figure out all the 
inputs - so check out the examples and documentation.

-Cramer


-----Original Message-----
From: A.Thome-08 at student.lboro.ac.uk 
[mailto:A.Thome-08 at student.lboro.ac.uk] 
Sent: Thursday, July 09, 2009 12:59 PM
To: trnsys-users at cae.wisc.edu
Subject: [TRNSYS-users] Control of on active layer



Good afternoon,

Within type 56, I created an embedded heating floor using an active 
layer.
But I don't manage to control it.

I would like the heating floor to operate only when the temperature of 
the room is below 20°C.

Which component should I use and how should I connect it.

Thank you very much.

Best regards,

Arnaud T.