Dear Arnaud,
In first hand, I think you can use Type34 to model your concrete overhang.
In the other hand, to model its effect on one part of the south west
facade, you may define two orientations in Type56
* SOUTH_WEST (for example) with direct south West orientation
* SHD_SW with South West orientation + Type 34 effect
Then, connect appropriate output between Type34 and Type56 to define IT,
IB and AI for both orientations, and put correct orientations on each
wall of your building.
Otherwise, you may simply use Type 34 "Fraction of solar shading" output
as "External Shading Factor" in Type56 to approximate shading effects on
South West windows concerned by this overhang.
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
87, Avenue de Chambéry
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
A.Thome-08 at student.lboro.ac.uk a écrit :
> Hi everybody.
>
> On the building I am modelling, there is some arcade on a part of the
> south-west facade. It is actually almost like an overhang but of course the
> material is not tissue but concrete.
>
> I would like to know if I can still use the overhang (type34) to model this?
>
> Secondly, in the case I would have to use Type34, I would like to know where
> can I specify that the shading is only ON ONE PART of the south-west facade
> ( not all of it).
>
> Thank you very much.
>
> Arnaud.
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> ---------------------------------------------------------------------------------------
> Orange vous informe que cet e-mail a ete controle par l'anti-virus mail.
> Aucun virus connu a ce jour par nos services n'a ete detecte.
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090715/8bcfe705/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 2884 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090715/8bcfe705/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list