Nicola,
The capacitance is the mass times the specific heat. Typically a good
first guess for a room is to multiply the volume of the room by 1.2
kg/m3 (to get the mass of the air) and then to multiply that value by
somewhere between 5 and 10. You are essentially saying that the air and
furnishings have a capacitance that is 5 to 10 times as much as the
capacitance of the air itself.
Kind regards,
David
Nicola Sorbi Unipg wrote:
>
> Dear all,
>
> How can I evaluate the capacitance of room air and its furnishings?
>
> Regards, Nicola.
>
>
>
> **
>
> * ** Dott. Ing. Nicola Sorbi*
>
> * *
>
> * UNIVERSITA' DEGLI STUDI DI PERUGIA*
>
> Dipartimento di Ingegneria Industriale
>
> Via G. Duranti 67 - 06125 Perugia
>
> Tel. +39 075/5853930 - Fax. +39 075/5853736
>
> E-mail nicolasorbi at mach.ing.unipg.it
>
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090108/8f9ea446/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4692 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090108/8f9ea446/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3625 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090108/8f9ea446/attachment-0003.jpeg>
More information about the TRNSYS-users
mailing list