[TRNSYS-users] TESS _ type 515 - season scheduler

David Bradley bradley at tess-inc.com
Mon Aug 17 13:51:31 PDT 2009


Feargal,
The description of that Type can be found in the ..\Trnsys16_1\Tess 
Models\Documentation\Applications Library\ directory. Essentially it has 
two outputs, one for "heating allowed" and one for "cooling allowed." To 
set up the component, click on the plugin icon at the bottom left of the 
proforma (see other threads if you have trouble doing this). The 
component outputs a "1" for the "heating allowed" output if the 
simulation time is within the defined heating season. Likewise, it 
outputs a "1" for the "cooling allowed" output if the simulation is 
within the defined cooling season. The outputs can be used as 
multipliers on other control signals to equipment that should be 
switched off during part of the year.
Kind regards,
David


Feargal Murray wrote:
> Hello
>
> How is the type 515 implemented into TRNSYS. What do you input to it and
> output from it?
>
> Thanks and regards,
>
> Feargal Murray
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************




More information about the TRNSYS-users mailing list