Arnaud,
In addition to Francois' comment, I am not sure how you are modeling the
building but if you are using Type56, make sure that you have set the
zone thermal capacitance to a realistic value. The thermal capacitance
defaults to 1.2 times the zone air volume, which takes into account only
the capacitance of the air in the zone. It neglects the capacitance of
furniture and fixtures. Typically, a value of about 5 to 10 times the
default is used. Changing that will result in a lot less oscillation for
your controller because the zone will respond more slowly (and more
realistically) to the heat pump.
Kind regards,
David
A.Thome-08 at student.lboro.ac.uk wrote:
> Good morning everyone,
>
> I connected Type 665 ( air/air heat pump) to the ventilation of type56.
> However, I don't manage to control properly the Heat pump.
>
> At the moment, the heat pump is control by a type 2 component. But it seems
> that there is a problem of information transmission between the heat pump
> and the controller.
>
> Enclosed, a file where it can be seen the controller setting and the heat
> pump working.
>
> Is it the best solution to connect the heat pump to the ventilation? Should
> I use the gains instead?
>
> Best regards,
>
> Arnaud.
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090804/6e87804b/attachment-0001.htm>
More information about the TRNSYS-users
mailing list