[TRNSYS-users] power coefficient of type 110
David Bradley
bradley at tess-inc.com
Tue Aug 4 08:44:15 PDT 2009
Claire,
yes, the power coefficients are the coefficients of the polynomial
that relates power to control signal. Typically, the values you would
use are a0=a1=0 and a2=1.
Kind regards,
David
claire kazgandjian wrote:
> Hi trnsys users,
>
> I would like to introduce a polynominal equation which link power and
> control signal of variable speed pump type 110, as shown in trnsys help :
> P = Prated * (a0 + a1*Ctrl + a2*ctrl²) with a0, a1, a2 polynominal
> coefficients.
>
> Does parameter 6 "power coefficient" correspond to "polynominal
> coefficient" ? (Indeed power coefficient unit is kJ/h and polynominal
> coefficient has no unit).
>
> If it's not the case, do you know what is "power coefficient"?
>
> Thank you!
>
> Claire
>
>
> ------------------------------------------------------------------------
> Vous voulez savoir ce que vous pouvez faire avec le nouveau Windows
> Live ? Lancez-vous !
> <http://www.microsoft.com/windows/windowslive/default.aspx>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090804/e2d5161c/attachment-0001.htm>
More information about the TRNSYS-users
mailing list