[TRNSYS-users] Question about take an output in time "t" as input in "t+1"
David Bradley
bradley at tess-inc.com
Wed Sep 10 07:31:05 PDT 2008
Camilo,
The simulation does not have enough thermal capacitance to solve - you
need to add a pipe (and perhaps a pump as well) so that the liquid
contained in your loop has enough mass that its temperature changes over
some time instead of instantaneously. Make sure that the pipe is big
enough to hold at least one timestep of fluid at your chosen flow rate.
I would also recommend making your tolerances smaller (they should be no
larger than 0.0001 instead of the default, which is 0.001) and running
with a smaller time step (I usually use 1 or sometimes minutes)
Kind regards,
David
Camilo Arias wrote:
> Hi
>
> I have de fallow problem: I need take an output simulation temperature
> in time "i" as input in the same system in time "i+1". I have a simple
> example, a auxiliar cooling unit connect to a new equation unit that
> take a energy amount and calculate the outlet temperature, this
> temperature is the input to the cooling unit again and the result are
> not good. I like know the correct form to solve this problem.
>
> Thank you
>
> regards
>
> Camilo Arias
>
> Pd: Attach the example
>
>
> ------------------------------------------------------------------------
>
> Yahoo! MTV Blog & Rock
> ¡Cuéntanos tu historia, inspira una canción y gánate un viaje a los
> Premios MTV!
> Participa aquí http://mtvla.yahoo.com/
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080910/292c2473/attachment-0001.htm>
More information about the TRNSYS-users
mailing list