Patrick,
Try NTYPE901 - its a solar balance on a given zone. An output file
will be generated by Type56 with all the terms of the solar balance as
described on page 6-26 of the 06-MultizoneBuilding manual. One thing to
be careful about is that each entry in the output file is the value of a
given energy transfer over the previous timestep. However, the values
are only generated once per hour. If you are able to run in energy rate
control and use a 1 hour time step, there is no problem but if you are
running with a shorter time step, you'll only be able to see the value
of the energy transfer over the last time step in the hour. Its a known
problem and one that will presumably be worked out in the next version.
Kind regards,
David
Patrick Wilkinson wrote:
>
> Hi,
>
>
>
> I am trying to find the total solar load into a typical office space.
> The typical office only has one window with a shade and is currently
> facing south. I am trying to determine the solar load based on
> different glazing/shades. What output in the TRNBuild model would I
> use to determine such a load to the space?
>
>
>
> Thanks for the help
>
>
>
> */Patrick Wilkinson/**/,/**/ /**/B.Sc. ENG,/**/ /**/LEED^® AP/**/
> Advanced Technology Group/**/
> /*
>
> 14130 Riverside Drive Suite 201
> Sherman Oaks, CA 91423
> p: (818) 377-8220 ext. 240
> f: (818) 377-8230
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> This e-mail message, including any attachments, is for the sole use of
> the intended recipient(s) and may contain confidential and privileged
> information. Any unauthorized review, use, disclosure, or distribution
> is prohibited. If you are not the intended recipient, please contact
> the sender by reply e-mail and destroy all copies of the original message
>
>
>
> .
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081006/37fd26cc/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1400 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081006/37fd26cc/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081006/37fd26cc/attachment-0003.jpeg>
More information about the TRNSYS-users
mailing list