Werner,
  lux (or lumens/m2) is a measure of luminous power as opposed to a 
measure of "pure" radiative power. A measure of pure radiative power 
weights all wavelengths of the radiation equally whereas measures of 
luminous power account for the fact that the eye is more sensitive to 
visible light wavelengths. There is certainly a relationship between the 
amount of solar radiation amount and the luminous radiation called the 
luminous efficacy. I have seen methods for calculating the luminous 
efficacy of certain window and skylight configurations but there is also 
a luminous efficacy associated with the atmosphere. If you run one of 
the TMY2 sites from the US, and look at the output for illuminance and 
solar radiation, you can divide one by the other and see what the 
general magnitude of the luminous efficacy is.
That was probably more informative than helpful...
Cheers,
 David


keilholz, werner wrote:
>
> Dear TRNSYS users,
>
>  
>
> I just ran into a weather data file with solar radiation data in 'lux'.
>
>  
>
> Now, that's even worse than the usual kj/hr.m^2... Illuminance (in lux 
> or cd/m^2) is a different dimension than Flux (in W/m^2), but one 
> might think there should be some relation between the two.
>
> Is there a way to compute (diffuse?) radiation from it?
>
>  
>
> Thanks,
>
> *Werner Keilholz**
> *TIDS / IIL / Ingénieur
>
> *Centre Scientifique et Technique du Bâtiment
> *84 avenue Jean Jaurès - Champs-sur-Marne - 77447 Marne-la-Vallée Cedex 2
> Tél : 04 93 95 67 46
> Fax : 04 93 95 67 33
> Port : 06 82 93 32 36
>
> *Évitez d'imprimer vos emails inutilement. Respectez l'environnement***
>
> *Ce message et toutes les pièces jointes sont confidentiels et 
> exclusifs pour le destinataire du message. N'importe quelle autre 
> distribution, utilisation ou reproduction est non autorisée et 
> interdite. Si vous receviez ce message par erreur, informez svp 
> l'expéditeur immédiatement et supprimez le message de votre système**.
> **
> **This message and any attachments are confidential, for the exclusive 
> use of the addressee and may be legally privileged. Any other 
> distribution, use or reproduction is unauthorised and prohibited. If 
> you received this message in error, please notify the sender 
> immediately and delete the message from your system.***
>
>  
>
>
>
>
>
> ************************************************************************************
> This footnote confirms that this email message has been scanned by
> PineApp Mail-SeCure for the presence of malicious code, vandals & 
> computer viruses.
> ************************************************************************************
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      2916 Marketplace Drive - Suite 104 
Partner                            Madison, WI 53719 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080624/c3c96c3a/attachment-0005.htm>


More information about the TRNSYS-users mailing list