[TRNSYS-users] Overhang Type 34
Hermann Schranzhofer
hermann.schranzhofer at tugraz.at
Mon Jun 23 12:25:44 PDT 2008
Hi Benoît Cogné,
as far as I know the problem is that type34 uses the isotropic sky model for calculating the diffuse radiation and there is no other possibility in type 34 (do not ask me why; maybe David Bradley can tell us more about that).
Type109 uses the Perez model to calculate the diffuse radiation. And this may cause the differences you got. You can check this by setting Parameter 3 of type109 to 1 (using the isotropic sky model). Than the results should be the same. For detail information of sky models there are a lot of papers available and you can also find some in the documentation of TRNSYS. The Mathematical Reference gives also some comparison and advises concerning the sky models:
(page 5-294):
"In general, the anisotropic sky models (Hay and Davies, Reindl, and Perez, et al) provide comparable estimates of the total radiation on a tilted surface and are recommended for general use. The Hay and Davies and the Reindl models are computationally simple when compared to the Perez model. The isotropic sky model (mode 1) under predicts the total radiation on a tilted surface and is not recommended for general use; it is included to permit consistency with simulations performed with earlier versions of TRNSYS."
We also had some troubles with that and we wonder why type34 does not give the possibility to choose the sky model.
Please, if I am wrong correct me (Bradley?)!
For your second problem, we use the connection type34<->type56 by creating additional orientations in TRNBUILD. There is an example shipped with TRNSYS called "SunSpace-Shading" showing you the correct connections.
I don't know if there are some differences using "fraction of solar shading" (type34) connected with "external shading factor" (type56).
I hope it helps a little bit and maybe someone else has more information.
Best regards
Hermann Schranzhofer.
_______________________________________________________________
DI Dr. mont. Hermann Schranzhofer
Institut fuer Waermetechnik / Institute of Thermal Engineering
TU Graz / Graz University of Technology
Inffeldgasse 25 / B, A-8010 Graz
Tel.: +43 316 873 7314
Fax : +43 316 873 7305
http://www.iwt.tugraz.at/
_______________________________________________________________
________________________________________
Von: B.Cogné - dH Technologies [mailto:benoit.cogne at dh-technologies.fr]
Gesendet: Montag, 23. Juni 2008 19:32
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] Overhang Type 34
Dear Trnsys users,
I am not fully experienced in Trnsys so my problem may be very simple to solve.
Trying to understand how to use the type 34 "Overhang" I made some tests and found strange results.
When Overhang and wingwall projections are set to zero, beam radiation and ground radiation to receiver are equal to same data from type 109. This is OK.
Sky diffuse is reduced a lot which does not look normal to me.
Is there an explanation ?
Here attached is this simple test
I also need some advice on the way to use the type 34 with the type 56.
Should I create in the building an orientation for each overhang and connect the type 34 outputs to the corresponding inputs or should I only use the fraction of solar shading from type 34 as the external shading factor of the window ?
I would appreciate an example on the way to connect type 34 properly to type 56
Looking forward for your help
Benoît Cogné
DH TECHNOLOGIES
France
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Hermann Schranzhofer.vcf
Type: application/octet-stream
Size: 208 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080623/a58d8600/attachment-0001.obj>
More information about the TRNSYS-users
mailing list