Cramer Silkworth
silkworth at transsolar.com
Thu Jul 31 09:26:20 PDT 2008
Amandine,
Check the thicknesses of your wall layers, layers that are too thin are
generally the cause of this error. If you've got any really thin layers,
consider using a massless layer and just define a resistance for it, as
its mass is probably negligible (which is why the transfer functions
freak out).
-Cramer
J. Cramer Silkworth
Transsolar Climate Engineering
Technical consulting for energy efficiency and environmental quality.
145 Hudson Street
Suite 402
New York, NY 10013
Office: 212-219-2255
Mobile: 347-283-2547
silkworth at transsolar.com
_____
From: Amandine Le Denn [mailto:amandine.le-denn at tecsol.fr]
Sent: Thursday, July 31, 2008 9:58 AM
To: trnsys-users at engr.wisc.edu
Subject: [TRNSYS-users] error creating a wall type Trnsbuild
Dear TNRSYS users,
I created walls in my TRNBuild simulation and an error message appears
when registering:"Error creating the wall transfert function
coefficients: Unable to find a root after indication that a root exists.
Maybe the timebase is too small. Please, check the INF-file further
information."
I do not see where is the problem. Thank you for your help.