Hello Ethan,

I am not familiar with Type 633, but you could try to connect the heat rate
output from the heater to the room input by adding new Gains in the Type 56
zone. There you can connect radiative and convective power from the heater,
choose the most appropriate, by input variables which you must first define
in the Type 56 building component. Thereafter you can connect appropriate
outputs from the heater to these inputs.

Since you mention that the heater has a fan, you can also connect it to the
room by adding a new Ventilation. I think this is the most common way of
specifying heating and cooling equipment outside of the building component.
Add air flow temperature, RH and room airchange rate as inputs to Type 56,
and connect them in the Ventilation setup. See Examples/HVAC-building on
how to do this.

Kind regards,
Knut Erik Enerstvedt



                                                                           
             trnsys-users-requ                                             
             est at engr.wisc.edu                                             
                                                                        To 
             02/11/2008 07:03          trnsys-users at engr.wisc.edu          
             PM                                                         cc 
                                                                           
                                                                   Subject 
             Please respond to         TRNSYS-users Digest, Vol 38, Issue  
             trnsys-users at engr         12                                  
                 .wisc.edu                                                 
                                                                           
                                                                           
                                                                           
                                                                           
                                                                           



----- Message from "Ethan Lust" <elust at umd.edu> on Mon, 11 Feb 2008
12:10:32 -0500 -----
                                                                           
        To: <trnsys-users at engr.wisc.edu>                                   
                                                                           
        cc: <trnsys-users-request at engr.wisc.edu>                           
                                                                           
   Subject: [TRNSYS-users] Help: connecting type 633 to type 56            
                                                                           

Hello,

I am just becoming familiar with TRNSYS and have come up against a problem
I can’t seem to work around.

I am trying to model a single room (type 56) with an electric space heater
(type 633), but I can't figure out how to link the heat rate output of the
heater to the room input.  The control signal is working appropriately as
is the heater (i.e. when room temperature drops, the control signal
activates the heater increasing the heat rate and fan power), but there is
no associated rise in space temperature.

Could someone point me in the right direction?

Thank you,
Ethan Lust
Graduate Research Assistant
University of Maryland
 _______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users





----------------------------------------------------------------------------------------------------------------------
NIVAs hovedkontor har flyttet til nye lokaler i CIENS - Forskningssenter
for miljø og samfunn; Gaustadalléen 21, 0349 Oslo. Meld deg på vårt
nyhetsbrev på www.niva.no




More information about the TRNSYS-users mailing list