Eleni,
Sorry for the delay in getting back to you. I think that "undisturbed"
in this case is just referring to the temperature of soil far enough
away from the building that it is not affected by anything other than
the time of year and depth. You can use the Type77 Ground Temperature
model to get the soil temperature. A good guess for the average annual
deep earth soil temperature is the average annual air temperature. The
amplitude is the difference between the maximum average monthly
temperature and the minimum average monthly temperature (you should be
able to figure that out from the data file). The shift is the day on
which the minimum temperature occurs and again should be obtainable from
the weather file.
Kind regards,
David
eleni ampatzi wrote:
> Dear All,
>
> I am using type 703 and I have a question regarding parameters 8,9,10
> which refer to the surface temperature- temperature of undisturbed
> soil. What does 'undisturbed soil' mean exactly? I can get
> measurements from local weather stations regarding the soil
> temperature at various depths; hourly values measured at 10cm depth,
> daily values taken at 9am for 30cm and 100cm depth.
>
> If I use average soil temperature measurements for 10cm depth, would
> that be a correct dataset to use in orfed to derive mean surface
> temperature, amplitude of surface temperature and day of min surface
> temperature? Would surface temperature differ a lot from the soil
> temperature at 10cm? Thank you in advance
>
> Best Regards
>
> Eleni
>
> --
> Eleni Ampatzi
> PhD Candidate
> Welsh School of Architecture
> Cardiff University
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081208/2252c812/attachment-0001.htm>
More information about the TRNSYS-users
mailing list