[TRNSYS-users] how to give the correct values for the type67?
Technical Support
TechSupport at tess-inc.com
Mon Apr 7 10:54:53 PDT 2008
Yujun,
I would suggest that you start out by drawing a plan-view of the shaded facade and of the surrounding obstacles that form the mask. Draw lines extending from the facade center point to the obstacles in even increments of surface azimuth angle. Determine the length of each of those lines between the facade and the obstacle. Next determine the height of the obstacle at the end point of each line. You now have two sides of a series of triangles. Type67 needs to know the angle between the horizontal line that you drew and the hypotenuse of each triangle.
Kind regards,
David
Technical Support TeamThermal Energy System Specialists, LLC2916 Marketplace Dr, Suite 104Madison, WI 53719techsupport at tess-inc.com
----- Original Message -----
Subject: [TRNSYS-users] how to give the correct values for the type67?
From: "Yujun TAO" >;aleck1314 at yahoo.fr>
Date: Mon, April 7, 2008 9:25
Dear users,I want to know how to give the correct values when create the external file for the type67.Can someone help me? Thanks in advanceYujun
Envoyé avec Yahoo! Mail.Une boite mail plus intelligente.
_______________________________________________TRNSYS-users mailing listTRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users