[TRNSYS-users] Wind loss modeling
David Bradley
bradley at tess-inc.com
Thu Sep 13 08:16:12 PDT 2007
John,
Most of the building models in TRNSYS simply ask for the user to
supply the external heat transfer coefficient so you can treat it
however you like. The algorithm that I usually use is from ASRHAE:
h = (AA+BB*WindVel+CC*WindVel**2)*3.6
where h is the external convection coefficient in kJ/h.m2, AA, BB,
and CC are empirical coefficients that depend on the exterior surface
material and WindVel is the wind speed in m/s. The AA, BB and CC
coefficients (again from ASHRAE) would be:
AA BB CC
Stucco 11.58 5.894 0.0
Brick 12.49 4.065 0.028
Concrete 10.79 4.192 0.0
Wood 8.23 4.00 -0.057
Smooth plaster 10.22 3.1 0.0
Glass 8.23 3.33 -0.036
Cheers,
David
At 13:30 9/12/2007, J.A. Palyvos wrote:
>Content-Type: multipart/alternative;
> boundary="----=_NextPart_000_0010_01C7F584.16361600"
>Content-Language: el
>
>Dear all,
>
>I would appreciate any information on the external forced convection
>algorithms (i.e. wind loss coefficient expressions) used in
>TRNSYS.(I am aware of the McAdams/Jurges linear relation used in Type 19).
>
>Many thanks,
>
>J.A. Palyvos, NTUA
>Athens
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070913/79830e1c/attachment-0001.htm>
More information about the TRNSYS-users
mailing list