<html>
<body>
John,<br>
  Most of the building models in TRNSYS simply ask for the user to
supply the external heat transfer coefficient so you can treat it however
you like. The algorithm that I usually use is from ASRHAE:<br><br>
h = (AA+BB*WindVel+CC*WindVel**2)*3.6<br><br>
where h is the external convection coefficient in kJ/h.m2, AA, BB, and CC
are empirical coefficients that depend on the exterior surface material
and WindVel is the wind speed in m/s. The AA, BB and CC coefficients
(again from ASHRAE) would be:<br><br>
<x-tab>        </x-tab><x-tab>
        </x-tab><x-tab>
        </x-tab>AA<x-tab>
      </x-tab>BB<x-tab>
      </x-tab>CC<br>
Stucco<x-tab>  </x-tab><x-tab>
        </x-tab>11.58<x-tab>
   </x-tab>5.894<x-tab>   </x-tab>0.0<br>
Brick<x-tab>   </x-tab><x-tab>
        </x-tab><x-tab>
        </x-tab>12.49<x-tab>
   </x-tab>4.065<x-tab>   </x-tab>0.028<br>
Concrete<x-tab>        </x-tab>
<x-tab>        </x-tab>
10.79<x-tab>   </x-tab>4.192<x-tab>
   </x-tab>0.0<br>
Wood<x-tab>    </x-tab><x-tab>
        </x-tab><x-tab>
        </x-tab>8.23<x-tab>
    </x-tab>4.00<x-tab>
    </x-tab>-0.057<br>
Smooth
plaster<x-tab>  </x-tab>10.22<x-tab>   </x-tab>
3.1<x-tab>     </x-tab>0.0<br>
Glass<x-tab>   </x-tab><x-tab>
        </x-tab><x-tab>
        </x-tab>8.23<x-tab>
    </x-tab>3.33<x-tab>
    </x-tab>-0.036<br><br>
Cheers,<br>
 David<br><br>
<br>
At 13:30 9/12/2007, J.A. Palyvos wrote:<br>
<blockquote type=cite class=cite cite="">Content-Type:
multipart/alternative;<br>
<x-tab>        </x-tab>
boundary="----=_NextPart_000_0010_01C7F584.16361600"<br>
Content-Language: el<br><br>
Dear all,<br>
 <br>
I would appreciate any information on the external forced convection
algorithms (i.e. <u>wind loss coefficient</u> expressions) used in
TRNSYS.(I am aware of the McAdams/Jurges linear relation used in Type
19).<br>
 <br>
Many thanks,<br>
 <br>
J.A. Palyvos, NTUA<br>
Athens<br>
 <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY                          
2916 Marketplace Drive - Suite 104 <br>
Partner                                       
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages: 
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>    
and     
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>