[TRNSYS-users] question about shad factor in building
David Bradley
bradley at tess-inc.com
Fri Nov 30 07:50:20 PST 2007
Yujun,
The internal and external shading factors in
TRNBuild reduce the amount of solar radiation
that passes through the window by multiplying the
radiation that you have specified as an input for
that window by the shading factor that is
specified. The factor affect beam and diffuse
radiation the same; if you specify a shading
factor of 0.5, then you will get exactly half of
the unshaded beam and diffuse radiation affecting
your zone. For external shading factors, the
incident radiation is reduced before passing
through the windows. For internal devices, the
energy balance is a bit different and the
reflectance of the device toward and away from
the zone (as specified in the window) comes into
play. There is some more information on this
energy balance in the 06-Multizone Building manual.
Kind regards,
David
At 06:04 11/30/2007, Yujun TAO wrote:
>Dear users,
>I don't understand clearly, Internal shad factor
>and External shad factor, in the definition the
>caractéristique of window. Does anyone could tell me the details?
>best regards
>
>TAO Yujun
>
>
>Ne gardez plus qu'une seule adresse mail !
><http://fr.rd.yahoo.com/mail/mail_taglines/trueswitch/*http://www.trueswitch.com/yahoo-fr/>Copiez
>vos mails vers Yahoo! Mail
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20071130/f29941f7/attachment-0005.htm>
More information about the TRNSYS-users
mailing list