Yujun,<br>
The internal and external shading factors in TRNBuild reduce the
amount of solar radiation that passes through the window by multiplying
the radiation that you have specified as an input for that window by the
shading factor that is specified. The factor affect beam and diffuse
radiation the same; if you specify a shading factor of 0.5, then you will
get exactly half of the unshaded beam and diffuse radiation affecting
your zone. For external shading factors, the incident radiation is
reduced before passing through the windows. For internal devices, the
energy balance is a bit different and the reflectance of the device
toward and away from the zone (as specified in the window) comes into
play. There is some more information on this energy balance in the
06-Multizone Building manual.<br>
Kind regards,<br>
David<br><br>
<br>
At 06:04 11/30/2007, Yujun TAO wrote:<br>
<blockquote type=cite class=cite cite="">Dear users,<br>
I don't understand clearly, Internal shad factor and External shad
factor, in the definition the caractéristique of window. Does anyone
could tell me the details?<br>
best regards<br><br>
TAO Yujun<br><br>
<br>
Ne gardez plus qu'une seule adresse mail !
<a href="http://fr.rd.yahoo.com/mail/mail_taglines/trueswitch/*http://www.trueswitch.com/yahoo-fr/">
Copiez vos mails</a> vers Yahoo! Mail <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>