[TRNSYS-users] Type703 slab on grade

David Bradley bradley at tess-inc.com
Fri Mar 30 07:44:05 PDT 2007


Fabien,
   If you have horizontal insulation directly underneath the entire slab 
then you would define that insulation in TRNBuild as a layer in the 
BOUNDARY wall that defines the slab. If you have insulation that extends 
vertically downward around the perimeter of the slab (like a skirt) then 
you define its R-value and the depth to which it extends using parameters 
17 and 18 of Type703. If you have horizontal insulation that extends 
outward from the perimeter of the slab or if you have horizontal insulation 
that extends inward from the perimeter but does not extend all the way to 
the middle of the slab then the effects of that kind of insulation is not 
calculated by Type703. If I am misunderstanding the type of insulation that 
you are considering, my apologies. Please feel free to send me a sketch of 
what you are trying to analyze and I will try to answer more clearly.
Cheers,
  David


At 11:36 3/27/2007, Fabien MELENEC wrote:
>Dear TRNSYS users,
>
>I am using the Type703 (slab on grade) and would like to know if this 
>component is able to take in consideration horizontal perimeter insulation.
>
>Best regards
>
>Fabien MELENEC
>Email  : <mailto:fabien.melenec at addenda.fr>fabien.melenec at addenda.fr
>
>Sté ADDENDA
>Service administratif et direction
>RN d'Auch
>32300 MIRANDE
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070330/0b454b8e/attachment-0005.htm>


More information about the TRNSYS-users mailing list