Fabien,<br>
If you have horizontal insulation directly underneath the entire
slab then you would define that insulation in TRNBuild as a layer in the
BOUNDARY wall that defines the slab. If you have insulation that extends
vertically downward around the perimeter of the slab (like a skirt) then
you define its R-value and the depth to which it extends using parameters
17 and 18 of Type703. If you have horizontal insulation that extends
outward from the perimeter of the slab or if you have horizontal
insulation that extends inward from the perimeter but does not extend all
the way to the middle of the slab then the effects of that kind of
insulation is not calculated by Type703. If I am misunderstanding the
type of insulation that you are considering, my apologies. Please feel
free to send me a sketch of what you are trying to analyze and I will try
to answer more clearly.<br>
Cheers,<br>
David<br><br>
<br>
At 11:36 3/27/2007, Fabien MELENEC wrote:<br>
<blockquote type=cite class=cite cite=""><font face="arial" size=2>Dear
TRNSYS users,<br>
</font> <br>
<font face="arial" size=2>I am using the Type703 (slab on grade) and
would like to know if this component is able to take in consideration
horizontal perimeter insulation.<br>
</font> <br>
<font face="arial" size=2>Best regards<br>
</font> <br>
<font face="arial" size=2>Fabien MELENEC<br>
Email :
<a href="mailto:fabien.melenec@addenda.fr">fabien.melenec@addenda.fr</a>
<br>
<br>
Sté ADDENDA<br>
Service administratif et direction<br>
RN d'Auch<br>
32300 MIRANDE<br>
</font> <br>
_______________________________________________<br>
TRNSYS-users mailing list<br>
TRNSYS-users@engr.wisc.edu<br>
<a href="https://www.cae.wisc.edu/mailman/listinfo/trnsys-users" eudora="autourl">
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users</a></blockquote>
<x-sigsep><p></x-sigsep>
****************************************************************************************<br>
Thermal Energy System Specialists (TESS), LLC <br>
David
BRADLEY
2916 Marketplace Drive - Suite 104 <br>
Partner
Madison, WI 53719 <br>
Phone: (608) 274-2577 USA <br>
Fax: (608) 278-1475 <br>
E-mail: bradley@tess-inc.com <br>
Web Pages:
<a href="http://www.tess-inc.com/" eudora="autourl">
http://www.tess-inc.com</a>
and
<a href="http://www.trnsys.com/" eudora="autourl">
http://www.trnsys.com<br><br>
</a>"Providing software solutions for today's energy engineering
projects" <br>
****************************************************************************************<br>
</body>
</html>