[TRNSYS-users] Forcing Functions and Weather Data Files
Diego A. Arias
daarias at wisc.edu
Mon Mar 19 15:09:50 PDT 2007
Hi Samuele,
The best solution is to use an equation, in which you use the function GT().
- Add an equation component in your project.
- Double click on the equation component, and add a new input, called
"Ib". You will connect the beam radiation from the radiation processor
to this input.
- Create another input called "cf". You will connect the output from the
forcing function Type14.
- Now, create a new equation:
cf2 = cf*GT(ib,0)
The function GT(a,b) returns 1 if a>b. You can find more information
about the available functions in the manual Volume7-Section7.6.9.
Best regards,
Diego
Samuele wrote:
> Dear all,
>
> I'm trying to simulate a simple system in which there is a pump and
> a linear parabolic concentrator but I don't have enough information for:
>
> - build a forcing function for the pump by which it can work from 6 am
> to 18 pm and only if beam radiation is higher than a fixed value;
>
> - update values of direct normal radiation in the weather data file,
> or create a new weather data file ( with inputs I would insert ) which
> could be read by Trnsys.
>
> Could anyone give me any advices?
>
> Thanks in advance,
> Samuele Mazzei.
> ------------------------------------------------------------------------
>