- build a forcing function for the pump by which it can work from 6 am to
18 pm and only if beam radiation is higher than a fixed value;
Use a Type 14 forcing function with the parameters
0,0 6,0 6,1 18,1 18,0 24,0
to set your daily repeating forcing function on between 6 and 18 and off
at other times during the day. Then use an equation card and multiply
this output from the forcing function by the function:
OK_Pump=GT(I_Beam,Value) ehere I_Beam is connected to the beam radiation
input. This should do the trick.
Jeff