Filippo,

>Myself i set the parameters very simply, (in order from the first to 
>the sixth) my values are:
>5
>1
>40
>26
>45
>43

the fourth parameter of Type8 is the cooling set point and the fifth 
parameter is the 1st stage heating set point. If the room temperature 
goes above the cooling set point, the controller turns the cooling 
system on and if the room falls below the heating set point, the 
controller turns on the heating system. The controller doesn't allow 
the cooling set point (16C in your case) to be lower than your 
heating set point (45C) because then both the heating and the cooling 
system would be on at the same time.