Filippo,<br><br>
<blockquote type=cite class=cite cite="">Myself i set the parameters very
simply, (in order from the first to the sixth) my values are: <br>
5<br>
1<br>
40<br>
26<br>
45<br>
43</blockquote><br>
the fourth parameter of Type8 is the cooling set point and the fifth
parameter is the 1st stage heating set point. If the room temperature
goes above the cooling set point, the controller turns the cooling system
on and if the room falls below the heating set point, the controller
turns on the heating system. The controller doesn't allow the cooling set
point (16C in your case) to be lower than your heating set point (45C)
because then both the heating and the cooling system would be on at the
same time.<br><br>
Cheers,<br>
 David<br><br>