Dear Roberto,
   It is my understanding that the "number of loops" indicates the number 
of parallel branches of piping that pass through the floor and that the 
total mass flow rate specified is divided equally among the number of loops 
that you have specified. I belive also that the empirical correlation used 
in the Type56 active layers was developed using various "typical" piping 
layouts. That might include perimeter zones and core zones, it might 
include your "straight through" configuration as well. If you want to use a 
radiant floor model that allows you to specify the path of pipes through 
the floor, you might look at Types701, 703, and 705 in the TESS Ground 
Coupling library.
Kind regards,
  David


At 08:39 10/27/2006, roberto-bruno\@libero\.it wrote:
>Dear all,
>I'd want to know if is possible to simulate a radiant system with 
>capillary pipes imposing laminar conditions for the fluid using prebid 
>4.0. I haven't understood the mean of "number of fluid loops" in active 
>layers definition. Are the pipes connectded by pipe coil with the same 
>value of mass flow rate or  the mass flow rate is divided by the number of 
>pipes in the floor? In fact, the aim of my job is to simulate a radiant 
>system where the pipes are in parallel and the mass flow rate is divided 
>in every pipe, in accordance with the attached picture.
>Any suggest is welcome.
>Best regards to all.
>
>------------------------------------------------------ Perdi 2 Taglie in 
>60 Giorni con Perdi Peso Cerotto! http://click.libero.it/perdipesocerotto3
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************





More information about the TRNSYS-users mailing list