Myting,
The Type56 output called QSENS is a positive value when there is a
cooling load and a negative value when there is a heating load in a given
zone. QCOOL and QHEAT are the same loads but are split apart so that
heating load is not a negative number. At any point in time during which
there is a cooling load QSENS and QCOOL should be equal. At any point in
time during which there is a heating load QSENS should be the negative of
QHEAT.
>I make a wall include a window without glass to adjacency to a another
>zone . TRNSYS calculate the air coupling automatically because of no glass?
no it will not. You need to provide the coupling air flow both from zone A
to zone B AND from zone B back to zone A. If you need a Type to compute the
amount of airflow, you can use Type157 (calling COMIS), Type97 (calling
CONTAM) the proformas for which are located in the Utility: Calling
External Programs directory in the TRNSYS Studio. Alternatively you can use
TRNFLOW.
Kind regards,
David
****************************************************************************************