Dear Guillaume,
Your error is a classical one when using very thin walls or very thick
walls. You just have to change the timebase in the outputs window in
trnbuild. For thin walls, timebase should be less than 1 and bigger than 1
for thick walls. In my projects, I often use thick walls and I often define
timebase = 3, 4 or 5 h.
Kind Regards,
Christophe.
At 21:20 31/01/2006, David Bradley wrote:
>Guillaume,
> When TRNBuild generates the Type56 files, it places the .inf, .bld, and
> .trn files all in the same location as the .bui file. If you aren't
> getting an .inf file when you save your .bui file, I would suggest that
> you send the .bui to your distributor to see if they can find the problem.
>
> As a side note, very thin walls as well as very thick walls can
> sometimes cause problems in generating the Type56 files. Interior wood
> doors or steel garage doors are often the offending walls.
>
>Kind regards,
> David
>
>
>At 08:06 1/31/2006, Guillaume Renault wrote:
>>Hi everybody,
>>I have defined my own walls, by using only layers already existing, saved
>>the walls in the user.lib.
>>When I want to save the project, an error message appears, which says
>>that I have to check the layer definition (thickness, ratio of
>>conductivity/ density) and to check the INF-File for further information.
>>
>>I checked the BUI file opened with a text reader, and I've found nothing
>>wrong.
>>All of the wall's thickness are less than 1 meter !
>>
>>Could someone tell me where is located the INF-File.
>>
>>Thanks in advance,
>>
>>_______________________________________________
>>TRNSYS-users mailing list
>>TRNSYS-users at engr.wisc.edu
>>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>****************************************************************************************
>Thermal Energy System Specialists (TESS), LLC
>David BRADLEY 2916 Marketplace Drive - Suite 104
>Partner Madison, WI 53719
>Phone: (608) 274-2577 USA
>Fax: (608) 278-1475
>E-mail: bradley at tess-inc.com
>Web Pages: http://www.tess-inc.com and http://www.trnsys.com
>
>"Providing software solutions for today's energy engineering projects"
>****************************************************************************************
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
===========================
ENERTECH
F-26160 FELINES SUR RIMANDOULE
tel-fax : 04 75 90 18 54
Email : sidler at club-internet.fr
Web : http://sidler.club.fr
================================
More information about the TRNSYS-users
mailing list