[TRNSYS-users] PMV output in combination with RELHUM output
hotline
hotline at transsolar.com
Wed Aug 2 03:31:57 PDT 2006
Nick,
actually for the calculation of the PMV the partial vapour pressure (and therefore the air humidity) is needed. Unfortunately TRNSYS sets the rel. humidity to 0 if it is not used and this causes an error in the PMV output.
We will fix this in Version 16. For Version 15 you will have to keep the relative humidity as an output in order to get the right PMV values.
Kind regards
Monika
-----Ursprüngliche Nachricht-----
Von: trnsys-users-bounces at engr.wisc.edu [mailto:trnsys-users-bounces at engr.wisc.edu] Im Auftrag von Nick van der Valk
Gesendet: Montag, 24. Juli 2006 10:03
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] PMV output in combination with RELHUM output
Dear TRNSYS users,
In a simulation of an office building, the values of the PMV output in TRNSYS 15 change depending on whether or not I add a RELHUM output in prebid. Without a RELHUM-output, the PMV values seem to be erroneous. Is this a bug, or am I doing something wrong?
Regards Nick
---------------------------------------------------------------
dr. ir. N.C.J. van der Valk
Cauberg-Huygen Raadgevende Ingenieurs BV
Bezoekadres: Boterdiep 48, 3077 AW ROTTTERDAM
Postadres: Postbus 9222, 3007 AE ROTTERDAM
Telefoon: 010 - 4 25 74 44
Fax: 010 - 4 25 44 43
Web: http://www.chri.nl <http://www.chri.nl/>
E-mail: mailto:n.vandervalk at chri.nl <mailto:n.vandervalk at chri.nl>
------- DISCLAIMER-------
Op deze e-mail is een disclaimer van toepassing:
A disclaimer is applicable to this e-mail, please refer to:
www.chri.nl/emaildisclaimer
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060802/8a6b73df/attachment-0001.htm>
More information about the TRNSYS-users
mailing list