[TRNSYS-users] about open window in building
David Bradley
bradley at tess-inc.com
Wed Apr 26 13:13:59 PDT 2006
Raj,
There are a number of ways that you can model an open window. The
simplest approach is to define a zone air change rate of infiltration for
when the window is open and then use a model (forcing function, controller,
etc.) to determine whether the window is open or closed at any given point
in the simulation. That of course leads to the question of how to determine
an appropriate air change rate when the window is open... there are two
methods for dealing with that; one uses a TRNSYS link with CONTAM, the
other uses a TRNSYS link with COMIS. The CONTAM link is built into the
standard TRNSYS 16 package. Basically, you download CONTAM from the NIST
website (it's free), assemble your building model in CONTAM and export that
model as a *.air file. You then add Type97 to your TRNSYS simulation.
Type97 is a Fortran implementation of CONTAM that calculates interzonal and
infiltration flow of air in the building. The flow rates calculated by
Type97 are passed to Type56 while zone temperatures are passed back to
Type97. If you decide to get into using CONTAM, I'd recommend getting the
latest TRNSYS version (16.1) as it has an enhanced version of Type97 that
allows you to modify the CONTAM air flow model as the simulation is running
instead of only allowing you to use a static air flow model as was the case
in the 16.0 release.
Kind regards,
David
At 12:26 4/26/2006, RAJ KUMAR wrote:
>Hello all,
>
> I want to simulate buiding(TYPE 56) with open window (window
> without glazing).
>Is it possible?. If so, kindly explain me.
>
> In another case, I find window(no glazing) type in window
> library, winid=10001and it is mentioned that U value is 5.8 W/m^2K. So I
> am getting difference in outside and inside sol air temperature
> of window,if I select win ID=10001.
>
> Can anyone help me?
>
>regards,
>Rajkumar.S
>
>
>Celebrate Earth Day everyday! Discover 10 things you can do to help slow
>climate change.
><http://us.rd.yahoo.com/mail_us/taglines/earthday/*http://earth.yahoo.com>Yahoo!
>Earth Day
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060426/b53435ba/attachment-0005.htm>
More information about the TRNSYS-users
mailing list