Dear Christophe:
The energy balance on a zone is given by:
BAL_ENERGY = -DQAIRdt + QHEAT - QCOOL + QINF + QVENT + QCOUP + QTRANS + 
QGINT + QWGAIN + QSOLGAIN
BAL_ENERGY should be always 0.
You can get many of these values using the optional outputs (NTYPES):
DQAIRdt --> DQAIR (NTYPE8)
QHEAT --> QHEAT (NTYPE30)
QCOOL--> QCOOL (NTYPE31)
QINF   --> QINF (NTYPE4)
QVENT --> QVENT (NTYPE5)
QCOUP --> QCOUP(NTYPE6)
QGINT -->  QGCONV(NTYPE7) + QGRAD(NTYPE13)
QWGAIN --> QTWG (NTYPE76)
QSOLGAIN --> QTABSI (NTYPE14) + QTABSO(NTYPE15)
The only variable that is not given as an optional output is QTRANS. 
But, as you have all of the other variables, it can be calculated from 
the energy balance.
Please let me know if this helps.
Best regards,
Diego
Enertech wrote:
> Dear Diego,
>
> Thanks for your solution. Even if it isn't the most cleanest solution, 
> I don't really care. But I think the most simplest solution would be 
> to obtain the same energy balance that in the file energy_zone.bal, 
> with direct outputs (see the second part of my email). I found the 
> equivalent output of QSOLGAIN : this is QTSABS (NTYPE75, see volume 6, 
> part 2, page 98), but I don't know how to obtain the equivalent output 
> (or combination of outputs) of QTRANS. Do you have an idea ?
>
> Kind Regards,
>
> Christophe
>
> At 17:07 08/11/2005, Diego A. Arias wrote:
>
>> Dear Christophe:
>>
>> Unfortunately, the renaming of the output files only occurs in files 
>> that have the same file name as the input file.
>>
>> An alternative could be to take advantage of the possibility that 
>> TRNSYS can be run from the command line.  If you type 'TRNExe.exe  
>> Input.dck', TRNSYS will start and execute the input file Input.dck  
>> This alternative allows you to run batch files.  For example, you can 
>> have in your batch file:
>>
>> "C:\Program Files\Trnsys16\Exe\TRNExe.exe" "C:\Program 
>> Files\Trnsys16\MyProjects\input1.dck" /N
>> "C:\Program Files\Trnsys16\Exe\TRNExe.exe" "C:\Program 
>> Files\Trnsys16\MyProjects\input2.dck" /N
>>
>> In this case, TRNSYS will start and run input1.dck, close, open again 
>> and run input2.dck.  The command /N tells TRNSYS not to display the 
>> dialog box at the end of the simulation.
>>
>> This may not be the cleanest solution, since you will have to create 
>> the input files by hand, but I do not know of another way to work out 
>> this problem.
>> Please let me know if you need additional information of how to 
>> implement this.
>> Best regards,
>>
>> Diego
>>
>> Enertech wrote:
>>
>>> Dear TRNSYS Users,
>>>
>>> In a building simulation study, I want to do a batch simulation by 
>>> changing automatically several parameters. So, I would like to use 
>>> TRNEDIT and a parametric table. My problem is that the file I want 
>>> to use,"Energy_zone.bal", is overwritten at each simulation and that 
>>> I don't know how to increment this file name.
>>>
>>> I know that the output file must have the same name that the *.trd 
>>> file to be incremented but I don't know how to change the name of 
>>> energy_zone.bal.
>>> As a solution, I'm trying to recalculate the data contained in the 
>>> file "energy_zone.bal" with direct outputs of the *.bui file, but I 
>>> don't know how to calculate QTRANS and QSOLGAIN (see volume 6 part 
>>> 2, page 103), these variables are not direct outputs.
>>> So, what do you think I should do ?
>>>
>>> Thanks a lot for your help.
>>> Christophe
>>>
>>> ===========================
>>> ENERTECH
>>> F-26160 FELINES SUR RIMANDOULE
>>> tel-fax : 04 75 90 18 54
>>> Email : sidler at club-internet.fr
>>> Web  : http://sidler.club.fr
>>> ================================
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at engr.wisc.edu
>>> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>>
>>
>>
>> -- 
>>
>> Diego A. Arias
>> TRNSYS Coordinator
>> Solar Energy Laboratory
>> University of Wisconsin - Madison
>> 1500 Engineering Drive
>> Madison, WI 53706
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at engr.wisc.edu
>> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
> ===========================
> ENERTECH
> F-26160 FELINES SUR RIMANDOULE
> tel-fax : 04 75 90 18 54
> Email : sidler at club-internet.fr
> Web  : http://sidler.club.fr
> ================================
>
    
    
More information about the TRNSYS-users
mailing list