[TRNSYS-users] problem with sky temperature model
Michaël Kummert
kummert at engr.wisc.edu
Tue Mar 8 15:14:10 PST 2005
Isabelle,
> Using Trnysys 16 with the Iisibat interface, I face one difficulty with
> the sky temperature model. Could you help me?
>
> The warning message I receive is the following:
>
> /** Warning at time : 6295.000000
> Generated by Unit : 12
> Generated by Type : 69
> TRNSYS Message 317 : The sky temperature model has reported an
> inconsistency in the supplied INPUTS. The inconsistency has been fixed
> but should be investigated as it may lead to other problems. This error
> can be caused by a dew point temperature above the ambient temperature,
> a solar radiation value less than zero, or a cloud cover fraction less
> than zero or greater than one
> Reported information : Not available
>
As indicated by the message, there are 4 conditions that can trigger
that warning:
- Dewpoint temperature > dry bulb temperature. This is easy to check
with a plot of the difference between your inputs 2 and 1. If this is
the cause, using both temperatures from Type 33 should make sure the
inputs are consistent.
- Direct or diffuse radiation < 0 (bad connection for input 3 or 4, or
bad data file)
- Cloud cover < 0 (Bad connection for input 5 or bad data file)
- Cloud cover > 1: Bad connection, likely because you use the output
from Type 89 directly. Type 89 outputs the cloud cover in
percents (i.e. 0..100) while Type 69 expects them between 0 and 1. You
have to use an equation between the 2 types (let's just say this is
for "historical reasons").
I hope this helps,
Michaël Kummert
PS: A bug has just been found in TRNSYS 16.00.0037 and before: Type 89
for EPW and CWEC files outputs the cloud cover between 0 and 10, not 0
and 100. This will be fixed in the next release.
--
_________________________________________________________
Michaël Kummert
Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706
Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert at engr.wisc.edu
SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys
More information about the TRNSYS-users
mailing list