[TRNSYS-users] Type 22
David Bradley
bradley at tess-inc.com
Thu Jul 21 06:56:31 PDT 2005
Krishna,
One solution could be that you use either Type93 or Type573 (in the TESS
Libraries) to delay the temperature you are monitoring by one time step and
then to control based on the delayed temperature. In order to do this, you
need to have a relatively small time step (on the order of 5 minutes or
less) but by controlling on the system values from one time step previous,
you are guaranteed to always be controlling based on a converged value.
Cheers,
David
At 09:18 AM 7/20/2005, Krishna wrote:
> I have a system with iterative feedback controller(Type 22) to
> control the flow rate based on the error signal(Temperature). In the
> secant method used by this type, one assumption would be that the error
> signal produced by a control signal is repeatable (so that the control
> signal can be interpolated). But it takes a few iterations for the system
> to give out a constant error signal(i.e Converged values) for a given
> control signal.
> This makes the secant method unusable unless we use the converged
> values to determine what the next control signal should be.
> One way to work over this could be that we check for convergence and
> the calculate the new control signal and then instruct trnsys that the
> system is not converged yet for the current time step and do this until
> the desired control signal is calculated.
>
>Could anyone please let me know if this is possible or if there is a
>better method to solve this problem.
>Thank you,
>krishna
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20050721/53e44d0d/attachment-0001.htm>
More information about the TRNSYS-users
mailing list