[TRNSYS-users] Type 34 shading device and additional external shading
Timo Sengewald
timo.sengewald at bls-energieplan.de
Fri Jul 9 05:39:04 PDT 2004
Arie,
thank you for this solution. I don't know if it is physically correct
but it seems to make sense and works fine.
Timo
_______________________________________________
Timo Sengewald
BLS Energieplan GmbH
Elsenstraße 106
D-12435 Berlin
Tel.: +49 30 53 32 81-0
Fax: +49 30 53 32 81-40
www.bls-energieplan.de
-----Ursprüngliche Nachricht-----
Von: Arie Kalkman [mailto:a.kalkman at chri.nl]
Gesendet: Freitag, 9. Juli 2004 11:57
An: 'Timo Sengewald'
Betreff: RE: [TRNSYS-users] Type 34 shading device and additional
external shading
Hi Timo,
I think you should not multiply the shading factors, but the
transmissions:
total transmission = (1- shading by type 34) * (1- shading by blinds).
the total shading now equals (1- total transmission)
regards, Arie.
-----Oorspronkelijk bericht-----
Van: Timo Sengewald [SMTP:timo.sengewald at bls-energieplan.de]
Verzonden: donderdag 8 juli 2004 14:34
Aan: TRNSYS-group
Onderwerp: [TRNSYS-users] Type 34 shading device and additional
external shading
Hello,
it is the first time I use Type 34 with Type 56 and until now everything
worked fine. But what I actually want to simulate is a window shaded by
slats at the facade (wingwall shading) and by an additional external
shading device (venician blinds). How can I combine the values resulting
from these two effects?
My two ideas were:
1 I can multiply (equation component or directly in the building
description) the shading factor calculated by type 34 with an additional
external shading factor (say 0.5). But the result can be 0 (no shading)
although the window is shaded.
2 I can add these two values which may result in a shading factor larger
than 1...
Type 34 has been discussed several times in the group but I did not find
any hints on that problem. Has somebody got an idea?
Thanks for your advice!
Timo
_______________________________________________
Timo Sengewald
BLS Energieplan GmbH
Elsenstra?e 106
D-12435 Berlin
Tel.: +49 30 53 32 81-0
Fax: +49 30 53 32 81-40
www.bls-energieplan.de
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
More information about the TRNSYS-users
mailing list