[TRNSYS-users] Type 34 shading device and additional external shading

Timo Sengewald timo.sengewald at bls-energieplan.de
Fri Jul 9 05:39:04 PDT 2004


Arie,

thank you for this solution. I don't know if it is physically correct
but it seems to make sense and works fine.

Timo

_______________________________________________
Timo Sengewald

BLS Energieplan GmbH
Elsenstraße 106
D-12435 Berlin
Tel.: +49 30 53 32 81-0
Fax: +49 30 53 32 81-40


www.bls-energieplan.de


-----Ursprüngliche Nachricht-----
Von: Arie Kalkman [mailto:a.kalkman at chri.nl] 
Gesendet: Freitag, 9. Juli 2004 11:57
An: 'Timo Sengewald'
Betreff: RE: [TRNSYS-users] Type 34 shading device and additional
external shading


Hi Timo,

I think you should not multiply the shading factors, but the
transmissions:

total transmission = (1- shading by type 34) * (1- shading by blinds).

the total shading now equals (1- total transmission)

regards, Arie.




-----Oorspronkelijk bericht-----
Van:	Timo Sengewald [SMTP:timo.sengewald at bls-energieplan.de]
Verzonden:	donderdag 8 juli 2004 14:34
Aan:	TRNSYS-group
Onderwerp:	[TRNSYS-users] Type 34 shading device and additional
external shading

Hello,

it is the first time I use Type 34 with Type 56 and until now everything
worked fine. But what I actually want to simulate is a window shaded by
slats at the facade (wingwall shading) and by an additional external
shading device (venician blinds). How can I combine the values resulting
from these two effects?

My two ideas were:

1 I can multiply (equation component or directly in the building
description) the shading factor calculated by type 34 with an additional
external shading factor (say 0.5). But the result can be 0 (no shading)
although the window is shaded.

2 I can add these two values which may result in a shading factor larger
than 1...

Type 34 has been discussed several times in the group but I did not find
any hints on that problem. Has somebody got an idea?


Thanks for your advice!


Timo

_______________________________________________
Timo Sengewald

BLS Energieplan GmbH
Elsenstra?e 106
D-12435 Berlin
Tel.: +49 30 53 32 81-0
Fax: +49 30 53 32 81-40


www.bls-energieplan.de


_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users






More information about the TRNSYS-users mailing list