Hi Daric,
I've struggled with this issue a lot too when I first started modeling;
what do you mean floor multipliers don't also apply to the HVAC systems?!
is this behavior correct with other’s experience?
Correct me if I'm wrong, but I believe HVAC system capacities should be
reflective of all respective zones *including *multipliers, rather than of
a single zone with no multipliers. For example, 30000 BTU/H should be
entered for the cooling capacity of an HVAC system with a zone of floor
multiplier 3, rather than 10000 BTU/H for the same zone.
There is no means within eQuest to specify a Systems multiplier?
I don't think there is a way to specify an HVAC system multiplier in
eQuest.
Hope this helps,
Calvin
On Tue, Aug 27, 2019 at 3:47 PM Daric Adair via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Fellow eQuesters;
>
> Am running into some confusion on the use of multipliers; and how the
> do/don’t appear to cascade out to HVAC Systems. If I create a 10 story
> building in the DD Wizard with ‘use multipliers’ checked and ‘HVAC System
> per Level’, this creates a building with the area of the 10 story building,
> on 3 floors, with 3 HVAC systems. Granted the middle floor has a floor
> multiplier of 8, which is linked to the spaces and zones – but not the
> systems. Thus, it is really 3 AHU’s – top, bottom, and a much larger AHU
> for the middle floor(s).
>
>
>
> I have been unable to find anything in the documentation that say ‘oh, by
> the way, this is floor multipliers don’t multiple HVAC Systems’ or ‘Don’t
> use this if you really do have multiple HVAC system.” Which is both odd,
> but unsurprising all at the same time.
>
>
>
> This approach could impact model performance, especially if performance
> curves do not scale in a multiplier fashion or if one is unaware of this
> behavior and looks up incorrect efficiencies based on the ‘multiplied’
> unit’s capacity. It also impacts reporting to LEED/Code if they see 3
> systems (from my example) and not the 10 AHU’s/RTU’s scheduled.
>
>
>
> Question is two part:
>
> 1. is this behavior correct with other’s experience?
> 2. There is no means within eQuest to specify a Systems multiplier?
>
>
>
> I see where multipliers *could* be used, but that isn’t my applciation
> here.
>
>
>
>
>
> Thanks,
>
> *DARIC R ADAIR* PE, CEM, BEMP
> Mechanical Engineer, Energy Analyst
>
> *Henderson Engineers*
> daric.adair at hendersonengineers.com
>
> hendersonengineers.com <http://www.hendersonengineers.com/>
>
> *Licensed in* KS
>
> *Sending me large files? Please use Henderson File Share
> <https://apps.hendersonengineers.com/FileShare/Upload?to=daric.adair@hendersonengineers.com>
> | TX ID #F-001236*
>
>
>
> ------------------------------
>
> This email and any files transmitted with it are confidential and are
> intended solely for the use of the individual or entity to whom they are
> addressed. This communication represents the originator's personal views
> and opinions, which do not necessarily reflect those of Henderson
> Engineers, Inc. If you are not the original recipient or the person
> responsible for delivering the email to the intended recipient, be advised
> that you have received this email in error, and that any use,
> dissemination, forwarding, printing, or copying of this email is strictly
> prohibited. If you received this email in error, please immediately notify
> administrator at hendersonengineers.com.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
*Calvin Chu, MFBA, EIT*
Energy Modeler
646-780-5536 | cchu at brightpower.com
www.brightpower.com
<http://www.brightpower.com/?utm_source=email&utm_medium=signature>
11 Hanover Square, 21st Floor
New York, NY 10005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/84dcbbfc/attachment.html>
More information about the Equest-users
mailing list