[Equest-users] eQuest Floor Multiplier vs System Multiplier
Nicholas Caton
Nicholas.Caton at se.com
Tue Aug 27 13:12:53 PDT 2019
Hi Daric!
The behavior you've described in your first paragraph has me nodding - sounds expected. But I think you're in luck today!
If you want a 'middle,' multiplied shell representing 7 levels to be served by 7 equally sized systems, then you need to specify NUMBER-OF-UNITS (and not be using a zonal system type to enable this input).
From: Volume 2: Dictionary > HVAC Components > SYSTEM > Simulation/Staging of Multiple Identical Air Handlers
[cid:image001.png at 01D55CE9.7DC70CF0]
[cid:image002.png at 01D55CE9.7DC70CF0]
[cid:image005.png at 01D55CE9.E3B939C0]
[cid:image005.png at 01D515A3.47EDD880]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image006.png at 01D515A3.47EDD880]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Daric Adair via Equest-users
Sent: Tuesday, August 27, 2019 2:47 PM
To: equest-users at onebuilding.org
Subject: [Equest-users] eQuest Floor Multiplier vs System Multiplier
[External email: Use caution with links and attachments]
________________________________
Fellow eQuesters;
Am running into some confusion on the use of multipliers; and how the do/don't appear to cascade out to HVAC Systems. If I create a 10 story building in the DD Wizard with 'use multipliers' checked and 'HVAC System per Level', this creates a building with the area of the 10 story building, on 3 floors, with 3 HVAC systems. Granted the middle floor has a floor multiplier of 8, which is linked to the spaces and zones - but not the systems. Thus, it is really 3 AHU's - top, bottom, and a much larger AHU for the middle floor(s).
I have been unable to find anything in the documentation that say 'oh, by the way, this is floor multipliers don't multiple HVAC Systems' or 'Don't use this if you really do have multiple HVAC system." Which is both odd, but unsurprising all at the same time.
This approach could impact model performance, especially if performance curves do not scale in a multiplier fashion or if one is unaware of this behavior and looks up incorrect efficiencies based on the 'multiplied' unit's capacity. It also impacts reporting to LEED/Code if they see 3 systems (from my example) and not the 10 AHU's/RTU's scheduled.
Question is two part:
1. is this behavior correct with other's experience?
2. There is no means within eQuest to specify a Systems multiplier?
I see where multipliers could be used, but that isn't my applciation here.
Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst
Henderson Engineers
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>
hendersonengineers.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.hendersonengineers.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7Ce542892419ae491b969708d72b275c82%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637025320369833077&sdata=nLWTb7sMziHaQK2rTeePt5GAMKQBG2qVqGC7YHkTTSU%3D&reserved=0>
Licensed in KS
Sending me large files? Please use Henderson File Share<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fapps.hendersonengineers.com%2FFileShare%2FUpload%3Fto%3Ddaric.adair%40hendersonengineers.com&data=02%7C01%7CNicholas.Caton%40se.com%7Ce542892419ae491b969708d72b275c82%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637025320369833077&sdata=JkPwTqZahs97ITgv%2FoVKVEm9o9RM5hhCCU%2FctXYzhsE%3D&reserved=0> | TX ID #F-001236
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com<mailto:administrator at hendersonengineers.com>.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 46220 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 44155 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 255 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 8477 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 62749 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190827/befea4fe/attachment-0004.png>
More information about the Equest-users
mailing list