Michael,
Have you entered input for HEAT-SET-T? If you leave it blank, you don’t get a main air-handler heating coil.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image007.jpg at 01D3BAB4.618608D0]  [cid:image008.jpg at 01D3BAB4.618608D0]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Monday, March 12, 2018 7:28 PM
To: equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] High unmet hours when selecting VAV system

Voila !!

Sounds like you need to have a reheat system defined. That happened to me a few times.

John Aulbach, PE

On Monday, March 12, 2018, 1:33:57 PM PDT, Michael Campbell via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:


Hi,
I'm having an issue where I get a very high number of unmet heating hours with space temps getting down as low as 33F in January.
This is only an issue when I select "Variable Air Volume" system which I believe is the correct system configuration.  It seems like the system is just failing to heat the space, but I cannot figure out why.  Has anyone has similar issues modeling a VAV system?
Thanks,
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/968981a8/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/968981a8/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/968981a8/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3856 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/968981a8/attachment.png>


More information about the Equest-users mailing list