[Equest-users] High unmet hours when selecting VAV system
Michael Campbell
mcamp1206 at gmail.com
Tue Mar 13 07:17:46 PDT 2018
Thanks for the help.
I defined the reheat system and set the thermostat type to Reverse Action
and I was able to get it to work.
On Tue, Mar 13, 2018 at 10:15 AM, Bishop, Bill <bbishop at pathfinder-ea.com>
wrote:
> Michael,
>
> Have you entered input for HEAT-SET-T? If you leave it blank, you don’t
> get a main air-handler heating coil.
>
> Regards,
>
> ~Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street
> <https://maps.google.com/?q=134+South+Fitzhugh+Street+%0D%0A+Rochester,+NY+14608&entry=gmail&source=g>
> Rochester, NY 14608
> <https://maps.google.com/?q=134+South+Fitzhugh+Street+%0D%0A+Rochester,+NY+14608&entry=gmail&source=g>
>
> *T: (585) 698-1956 <(585)%20698-1956>* F: (585)
> 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *John Aulbach via Equest-users
> *Sent:* Monday, March 12, 2018 7:28 PM
> *To:* equest-users <equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] High unmet hours when selecting VAV system
>
>
>
> Voila !!
>
>
>
> Sounds like you need to have a reheat system defined. That happened to me
> a few times.
>
>
>
> John Aulbach, PE
>
>
>
> On Monday, March 12, 2018, 1:33:57 PM PDT, Michael Campbell via
> Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
>
>
>
> Hi,
>
> I'm having an issue where I get a very high number of unmet heating hours
> with space temps getting down as low as 33F in January.
>
> This is only an issue when I select "Variable Air Volume" system which I
> believe is the correct system configuration. It seems like the system is
> just failing to heat the space, but I cannot figure out why. Has anyone
> has similar issues modeling a VAV system?
>
> Thanks,
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/37c4e3fa/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/37c4e3fa/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/37c4e3fa/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3856 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180313/37c4e3fa/attachment.png>
More information about the Equest-users
mailing list