[Equest-users] Equipment Load
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Thu Dec 20 09:36:31 PST 2018
It does make sense!
In support of the limits for my brain’s memory capacity, I like to insert that sort of algebra to distribute your input assumptions into the fields as a local expression to retain the logic for me in lieu of separate development notes outside the model.
~Nick
[cid:image001.png at 01D49858.3EEBECE0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D49858.3EEBECE0]
From: Jing Hong <hongjing.shirley at gmail.com>
Sent: Thursday, December 20, 2018 11:25 AM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: Paul Diglio <paul.diglio at sbcglobal.net>; equest-users at onebuilding.org
Subject: Re: [Equest-users] Equipment Load
[External email: Use caution with links and attachments]
________________________________
Thank you Nick. Yes, after trying different ways, I realized that fill “ Input Power” is better than per area. I assumed 20% of the input power would be converted to heat gain. And 80% for sensible, 20% for latent. In that case, the fraction I filled in the eQuest was 0.16 for sensible HG and 0.04 for Latent HG. Does that make sense?
Jing
On Wed, Dec 19, 2018 at 10:09 PM Nicholas Caton <Nicholas.Caton at schneider-electric.com<mailto:Nicholas.Caton at schneider-electric.com>> wrote:
Great thread!
@Jing: You definitely have some options in terms of how you use the inputs to account for installed vs. "thermally incident on the space" energy. I personally prefer to use the "Input Power" field to represent the maximum "installed" watts/gas input, then use the "fraction to space" to capture how much isn't carried away by the hood(s). From there, the associated fractional schedule(s) will dictate both what is seen over time at the meter and in the space.
@All: The COMnet appendix C schedules don't appear at my first glance to expressly cover kitchen equipment profiles, but rather appear to "dodge" the issue with the statement for refrigeration/gas equip of "COMNET defaults are based on continuous operation." Perhaps digging into those defaults might reveal some effective FLE hours of operation for a given kitchen? Another avenue may be to research whatever current operational schedule guidance might via Fisher-Nickel (Fishnick) for LEED prescriptive measures - resources I believe are linked from here: https://fishnick.com/design/resources/leed/<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Ffishnick.com%2Fdesign%2Fresources%2Fleed%2F&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ca014a794b4a6431914e608d666a01e28%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636809235216612795&sdata=3fLLR4roRf9sI96wATsV1ailuOlCc9fWpfg22qWuwv8%3D&reserved=0>
~Nick
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
-----Original Message-----
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Paul Diglio via Equest-users
Sent: Tuesday, December 18, 2018 8:51 AM
To: Paul Diglio <paul.diglio at sbcglobal.net<mailto:paul.diglio at sbcglobal.net>>; Jing Hong <hongjing.shirley at gmail.com<mailto:hongjing.shirley at gmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>; equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: Re: [Equest-users] Equipment Load
[External email: Use caution with links and attachments]
________________________________
Hi Jing:
Yes, as long as you have documentation to back up your estimate, I would use 20% of the electrical and gas energy as being rejected in the space. The tables look good to me. I don't know what your schedule looks like. Attached is the COMnet schedules that are usually accepted by the rating authorities.
Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
--------------------------------------------
On Tue, 12/18/18, Jing Hong <hongjing.shirley at gmail.com<mailto:hongjing.shirley at gmail.com>> wrote:
Subject: Re: [Equest-users] Equipment Load
To: "Paul Diglio" <paul.diglio at sbcglobal.net<mailto:paul.diglio at sbcglobal.net>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>, equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>, equestuser00 at gmail.com<mailto:equestuser00 at gmail.com>
Date: Tuesday, December 18, 2018, 9:29 AM
Hi
Paul,
For our cases, we
estimated 80-ish% of the heat will go right up to the exhaust hood. So should I fill the equipment and internal energy energy sources with the number before the 80% reduction or after? For example, I have 10 W/sqft electricity cookers and 100,000 Btu/hr gas cookers in the kitchen, do I fill the tables below correctly?
On Tue, Dec
18, 2018 at 6:38 AM Paul Diglio <paul.diglio at sbcglobal.net<mailto:paul.diglio at sbcglobal.net>>
wrote:
Jing:
Usually there is an exhaust hood with makeup air in the kitchen. If this is true, then you need to estimate how much heat is actually transmitted to the space compared to how much heat is expelled through the hood. This should lower your cooling load.
Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
--------------------------------------------
On Mon, 12/17/18, Jing Hong via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
wrote:
Subject: [Equest-users] Equipment Load
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>,
equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>,
equestuser00 at gmail.com<mailto:equestuser00 at gmail.com>
Date: Monday, December 17, 2018, 7:37 PM
Dear
All,
I have a question regarding
the internal load.
Under the Equipment tab of
the internal load, there are two tables. One is Equipment
and another is Internal Energy Sources. For my project with
a kitchen serving 5 hours daily, how to input the power?
For example, based on the specification sheets, we have
26.5 W/sqft input power density for electricity, and
474,000 Btu/hr for gas equipment. However, it will make the
cooling load so huge for cooling
systems. Does anyone know
how eQuest convert energy input to cooling load? Did I fill
the tables right?
Thank
you!Jing_______________________________________________
Equest-users mailing list
https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Cda94ce53bbe8407355ee08d664f84c50%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636807415798796966&sdata=L72FkkZxXrBbwaoKUamhTRFb1Y%2FcDZ7AeBUt0cIBbXY%3D&reserved=0<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ca014a794b4a6431914e608d666a01e28%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636809235216612795&sdata=vfI6%2Fu19p9etze7fCrXDsryIPT6RwHVMu7dkQOE1SdI%3D&reserved=0>
To unsubscribe from this mailing list send a blank
message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-----Inline Attachment Follows-----
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/3ff94610/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/3ff94610/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/3ff94610/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7123 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/3ff94610/attachment.obj>
More information about the Equest-users
mailing list