[Equest-users] Modeling ERVs that use air from multiple zones
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Tue Mar 28 11:28:13 PDT 2017
I'd first consider grouping all restroom zones + the serving corridor zone(s) under a single "corridor" system in your model. This allows ERV inputs specified in one place only, and simplifies specifying heating-only between the system inputs and control zone(s)' thermostat schedules for the needed OA pre-conditioning.
Think about whether the restrooms actually received pre-heated corridor air vs. something "more conditioned." This might not be a perfect fit if the restrooms' conditioned makeup actually comes from cooled spaces or directly from other AHU's... but this would be a starting point in that case and the differential in terms of what's seen at the ERV might not be meaningful enough to get worked up about.
You could also go down a path of replicating/weighting ERV inputs between the affected systems instead, but I suspect that would probably end up being much more work than the above alternative for your scenario.
Getting exhaust/relief loads transposed between systems to be seen with ERV is indeed tricky, but an explored path with a destination at least. It entails quantifying the hourly sensible/latent loads you mean to transpose, and spoon-feeding those loads into a space under the receiving ERV via a "free" hourly process schedule. This is done most commonly I think in concert with the OA-FROM-SYSTEM + "dummy zone" approaches to tackle DOAS that also involves heat recovery equipment, if anyone needs some search terms to find related threads in the archives.
~Nick
[cid:image001.png at 01D2A7C7.255650F0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D2A7C7.255650F0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Saaf, Paula via Equest-users
Sent: Tuesday, March 28, 2017 12:35 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Modeling ERVs that use air from multiple zones
Hi All,
How do you model an ERV that is using exhaust air from toilet exhaust that comes from multiple zones? The toilets are in zones that are associated with different AHUs. The ERV is providing fresh air to a corridor. There is a hot water coil in the ERV. That's the only "conditioning" the air gets.
Looking at Nicks sketch in the Energy Recovery Wheel on VAV System - zonal exhaust thread it appears that eQuest cannot use exhaust air from one zone to an ERV that is attached to another zone.
Thanks for you input.
Best regards
for KEMA Inc
Paula Saaf P.E.
Engineer, Middletown
paula.saaf at dnvgl.com<mailto:paula.saaf at dnvgl.com>
Direct +1 860 3465001
dnvgl.com<http://dnvgl.com/> | LinkedIn<http://www.linkedin.com/company/dnvgl>
[DNV GL]<http://www.dnvgl.com/>
This message may contain confidential or private information. If you are not the addressee, please return the message to its sender and delete it from your files. Please consider the environment before printing this email.
**************************************************************************************
This e-mail and any attachments thereto may contain confidential information and/or information protected by intellectual property rights for the exclusive attention of the intended addressees named above. If you have received this transmission in error, please immediately notify the sender by return e-mail and delete this message and its attachments. Unauthorized use, copying or further full or partial distribution of this e-mail or its contents is prohibited.
**************************************************************************************
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170328/8679d3b7/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170328/8679d3b7/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20170328/8679d3b7/attachment-0005.png>
More information about the Equest-users
mailing list